- Question Title: Help with install of exhaust fan on vent duct
- Asked by: Guest
- Asked On:
- Answers: 1
Hello,
we are going to install exhaust fan on ventilation duct. Kindly, provide us technical description i.e. flow rate of oil cooler fan for 90 KW oil injected atlas copco compressors
Waiting for prompt response
Thanks
Answers & Replies
Log in or create an account to make a comment...
I'm not sure where it is exactly you want to install this exhaust fan.
For Atlas Copco compressors, generally they say the maximum pressure drop in the ducts can be 30 Pa (= 0.0003 bar). If it is more, an outlet fan is needed on the end of the ducts.
In the Atlas Copco manual for a GA90 they say the maximum air speed through the (cooling air) grids is 5 meters/sec.
The most important things to keep in mind:
Best way to make sure of this is to use ducting for inlet air, for outlet air or for both.
Please see picture for screenshot from the manual. I would not recommend installation proposal 1 in hot countries!
And I attached 1 more screenshot with some more information from Atlas Copco.
Good luck!